December 19, 2011 By ©2007-2012Author - Licensed Electrical Contractor Filed under No Power

Cause of No Power to a Home Electrical Circuit

Cause of No Power to a Home Electrical Circuit

 

Causes of No Power to an Outlet or Light Circuit

I have one room circuit with no electrical circuit power.

  • The hallway lights have no power. One outlet in the living room has no power.
  • The doorbell ringer, and smoke detector, located in the hallway, are not working.
  • I have replaced two circuit breakers,three outlets, and two light switches.
  • I have no idea whats going on.

This electrical question came from: Rick, a Homeowner from Georgetown , Kentucky.
See more about Home Wiring for Kentucky

Dave’s Reply:
Thanks for your electrical question Rick.

Identifying the Cause of a Lost Power to an Electrical Circuit

  • Rick, if this is a problem that affects more than one circuit then the problem may be at the panel.
  • However from what you are describing the problem is most likely at a main junction box where there may be a burnt wire connection, which is commonly the neutral that has burnt loose because of a deteriorating connection over time.
  • This calls for going through a process of troubleshooting in order to identify the problem.
  • The problem may be located in a ceiling light fixture junction box where the light fixture is mounted close to the ceiling.
  • The heat from the light fixture can travel up into the junction box and cause the insulation of the electrical wring to become brittle and eventually an electrical splice may come apart and fail.

The Following links will assist you with your electrical circuit:

electrical outlet wiring
outlet-wiring

  • Wiring Electrical Outlet for the Home
  • Home electrical wiring includes 110 volt outlets and 220 volt outlets and receptacles which are common place in every home. See how wiring electrical outlets for the home are done.

electrical circuit
home-electrical-circuits

  • Electric Circuit Listing
  • The size of the home electrical service panel is designed by calculating the square footage of the home and factoring in the code requirements for the electrical circuits that are required.

circuit breaker
2-pole-circuit-breaker

  • Electrical Wiring Protection using Circuit Breakers
  • A guide to home electrical circuit breakers and how they work to protect your electrical wiring. When properly installed, your home electrical wiring is protected by a circuit protection device.

 


Be Careful and Be Safe - Never Work on Energized Circuits!
Consult your Local Building Department about Permits and Inspections for all projects.
For Best Results Consult a Licensed Electrical Contractor in Your Area

Comments

2 Responses to “Cause of No Power to a Home Electrical Circuit”
  1. Dave Rongey says:

    Shawn,
    The outlet that the vacuum was plunged into may have a bad wiring connection, or a splice for that circuit may be going bad. The circuit should be turned off so the outlet can be removed and inspected. Repair of the affected wiring will be required, and or replacing the outlet.
    Dave

  2. my son plugged in and turned the vacuum on in his room and the power went off in his room and to one socket in the front room it happened once before and it eventually started working i’ve tried turning the breaker off on back on but didn’t but the breaker didnt’t show its was blown any way so what should i do THANKS


* Please Use This Link to Ask the Electrician a Question using the Question Form. Thank You!

Thanks for Your Comments about this Article or the Website


FOR THE BENEFIT OF ALL: